Electrician question - Voltage coming through an off switched outlet.

I noticed a low voltage (florescent) bulb in a lamp flickering last night after the wall switch was turned off. Could not believe this was happening so I measured the voltage coming directly from the outlet and it measured about 10% of the regular voltage.

Something does not seem right! Can anyone explain this?

Dano
Tampa, Fl.

12 K1600 GTL
02 K1200 LT (gone but not forgotten)
DanDiver is offline  
Sponsored Links
Advertisement
 
post #2 of 15 Old Sep 6th, 2012, 4:58 pm
Lifetime Supporter
 
sperra's Avatar
 
Join Date: Sep 2008
Location: Ivoryton, CT, United States
Posts: 142
Re: Electrician question - Voltage coming through an off switched outlet.

Time for a new switch ? maybe a mouse removal


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
sperra is offline  
post #3 of 15 Old Sep 6th, 2012, 6:35 pm
Senior Member
 
dshealey's Avatar
 
Join Date: Apr 2002
Location: Dandridge (Near Knoxville), TN, USA
Posts: 12,165
Re: Electrician question - Voltage coming through an off switched outlet.

One possibility is that something else up the chain is on, and too many connections in the neutral (white) wire between that and the electrical panel. A voltage drop can show up in the neutral line can show up as voltage in a light fixture.

Use your volt meter to test between the white wire and a good ground, it normally should be at or very near zero. If more than that, you have "dirty" neutral wiring.

One common cause is a "non solid" neutral, with it open at some point. White neutral wires should never be seperated in a fixture so that removing them from the fixture results in an "open" neutral. Anywhere a neutral circuit is wired into a fixture, switch, etc., it should be with a pigtail crimped or wire nutted to the two white wires coming into the box. Most fixtures will not have more than one, unless fixtures are in parallel.

I have seen people put the two white wires under the screws on a switch or fixture, but removing them to replace the device leaves other devices upstream without a return, and can be dangerous.

I don't want to achieve immortality through my work...I want to achieve it through not dying.

David Shealey
Dandridge, TN
EX: '01 Black LT, BAT BYKE (Totaled at 110,000 miles)
IBA SS, BB, BBG, 10/10ths.
No bike now, but maybe in the future.
dshealey is offline  
 
post #4 of 15 Old Sep 6th, 2012, 7:25 pm
Lifetime Supporter
 
deanwoolsey's Avatar
 
Join Date: Aug 2008
Location: Topeka, KS, USA
Posts: 3,105
Re: Electrician question - Voltage coming through an off switched outlet.

What David said. Got me a big surprise one day changing out a ceiling fan. Someone had wire nutted several neutral wires together and I found the live return when I took the nut off to attach the fan. OUCH!!!!!


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
deanwoolsey is offline  
post #5 of 15 Old Sep 6th, 2012, 7:44 pm Thread Starter
Senior Member
 
DanDiver's Avatar
 
Join Date: Jun 2003
Location: Tampa, FL, USA
Posts: 4,830
Re: Electrician question - Voltage coming through an off switched outlet.

Thanks David,

I'll pull the switch first and then check to see if it looks ok. My guess is that there is a neutral not connected correctly. I have noticed that plugs in the same outlet spark when plugged in.

Dano
Tampa, Fl.

12 K1600 GTL
02 K1200 LT (gone but not forgotten)
DanDiver is offline  
post #6 of 15 Old Sep 6th, 2012, 11:08 pm
Member
 
LJSMITH1's Avatar
 
Join Date: Oct 2005
Location: Stamford, CT, USA
Posts: 93
Re: Electrician question - Voltage coming through an off switched outlet.

Is there a dimmer somewhere in the circuit? If so, check to see if it has a nightlight feature on the dimmer (a small neon glow behind the button or rocker when off). If so, this is the source of your Voltage.

2005 BMW K1200LT Blue
BMWMOA #124788

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Predecessor:
1999 K1200LT (entered the BMW "organ donation program" on 6/2/11) 38,256 Miles
LJSMITH1 is offline  
post #7 of 15 Old Sep 7th, 2012, 7:18 am Thread Starter
Senior Member
 
DanDiver's Avatar
 
Join Date: Jun 2003
Location: Tampa, FL, USA
Posts: 4,830
Re: Electrician question - Voltage coming through an off switched outlet.

Quote:
Originally Posted by LJSMITH1
Is there a dimmer somewhere in the circuit? If so, check to see if it has a nightlight feature on the dimmer (a small neon glow behind the button or rocker when off). If so, this is the source of your Voltage.

No dimmer. There is a wall switch that controls 1/2 of a two prong outlet. My guess now is that there is a bad ground or white wire possible in the two prong outlet. It really is spooky to have the switch off and the lamp flickering!

Dano
Tampa, Fl.

12 K1600 GTL
02 K1200 LT (gone but not forgotten)
DanDiver is offline  
post #8 of 15 Old Sep 7th, 2012, 8:49 am
Lifetime Supporter
 
DanMartin's Avatar
 
Join Date: Jun 2002
Location: Fulshear, TX, USA
Posts: 2,082
Re: Electrician question - Voltage coming through an off switched outlet.

Quote:
Originally Posted by DanDiver
No dimmer. There is a wall switch that controls 1/2 of a two prong outlet. My guess now is that there is a bad ground or white wire possible in the two prong outlet. It really is spooky to have the switch off and the lamp flickering!
How do you get a switch to only control half of an outlet?
I thought there was one inlet for both plugs.
DanMartin is offline  
post #9 of 15 Old Sep 7th, 2012, 9:50 am
Lifetime Supporter
 
johnbaker15's Avatar
 
Join Date: Sep 2010
Location: Chelmsford, Ma, USA
Posts: 1,595
Re: Electrician question - Voltage coming through an off switched outlet.

DanMartin,

If you look at the outlet on the side there is a break off tab. Wire the power to bottom of the outlet, break off the tab and wire the switch to top of the outlet.

Most all room entry switches that do not control an overhead light are wired to a wall outlet and swith the top of the outlet. HTH

John Baker

2005 BMW K1200LT
1979 Suzuki GS1000E
1978 Honda CB350
1975 Suzuki GT380
johnbaker15 is offline  
post #10 of 15 Old Sep 7th, 2012, 1:06 pm Thread Starter
Senior Member
 
DanDiver's Avatar
 
Join Date: Jun 2003
Location: Tampa, FL, USA
Posts: 4,830
Re: Electrician question - Voltage coming through an off switched outlet.

Quote:
Originally Posted by DanMartin
How do you get a switch to only control half of an outlet?
I thought there was one inlet for both plugs.
We have a lot of them like that. Switch controls several lamps in the room but does not turn off things plugged into the top. Works well, most of the time!

Dano
Tampa, Fl.

12 K1600 GTL
02 K1200 LT (gone but not forgotten)
DanDiver is offline  
post #11 of 15 Old Sep 7th, 2012, 8:01 pm
Lifetime Supporter
 
johnbaker15's Avatar
 
Join Date: Sep 2010
Location: Chelmsford, Ma, USA
Posts: 1,595
Re: Electrician question - Voltage coming through an off switched outlet.

Quote:
Originally Posted by DanDiver
We have a lot of them like that. Switch controls several lamps in the room but does not turn off things plugged into the top. Works well, most of the time!
Dan,
Must be a regional thing...north vs south.

John Baker

2005 BMW K1200LT
1979 Suzuki GS1000E
1978 Honda CB350
1975 Suzuki GT380
johnbaker15 is offline  
post #12 of 15 Old Sep 7th, 2012, 8:17 pm
Senior Member
 
dshealey's Avatar
 
Join Date: Apr 2002
Location: Dandridge (Near Knoxville), TN, USA
Posts: 12,165
Re: Electrician question - Voltage coming through an off switched outlet.

Quote:
Originally Posted by DanDiver
We have a lot of them like that. Switch controls several lamps in the room but does not turn off things plugged into the top. Works well, most of the time!
That is the way most electricians will wire them, bottom switched, top always hot. Lamps plugged into the bottom switched, allowing easier plugging in other items (better visibility on top rather than reaching under the lamp wires).

I don't want to achieve immortality through my work...I want to achieve it through not dying.

David Shealey
Dandridge, TN
EX: '01 Black LT, BAT BYKE (Totaled at 110,000 miles)
IBA SS, BB, BBG, 10/10ths.
No bike now, but maybe in the future.
dshealey is offline  
post #13 of 15 Old Sep 8th, 2012, 7:39 am
Senior Member
 
mtrevelino's Avatar
 
Join Date: Apr 2002
Location: Williamsburg, VA, USA
Posts: 2,528
Re: Electrician question - Voltage coming through an off switched outlet.

Quote:
Originally Posted by dshealey
That is the way most electricians will wire them, bottom switched, top always hot. Lamps plugged into the bottom switched, allowing easier plugging in other items (better visibility on top rather than reaching under the lamp wires).
Also, in most newly constructed homes, the electrician will turn the receptacle around, so all the "normal" receptacles will have the ground at the bottom on the hot and neutrals, while the combination plug will have the ground on top of the hot and neutrals. This way you can walk into a room and immediately tell which outlet is controlled by a wall switch.

Mike Trevelino
Williamsburg, VA
2008 RT
2000 LT - Totaled at 99,960 miles


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
mtrevelino is offline  
post #14 of 15 Old Sep 8th, 2012, 9:19 pm
Senior Member
 
Join Date: Sep 2006
Location: MARCO ISLAND, FL, W. NC USA
Posts: 1,178
Re: Electrician question - Voltage coming through an off switched outlet.

Dan, pull the wires from the switch and then check voltage, we get small sugar ants in Fl and they love switch devices. Ping me if you get stumped. I am a state Mechanical contractor & Master Electrician. Don't ignore this.

2013 BMW Damask Red K1600GTL
2014 BMW K1600GTL-E EXCLUSIVE
2001 Honda C-250 Helix
SOLD 2006 BMW K-1200LT "The Manatee"

Smokin'


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
SmokinJoe is offline  
post #15 of 15 Old Sep 9th, 2012, 2:39 pm
Senior Member
 
gunny's Avatar
 
Join Date: Aug 2003
Location: Kings Mountain, NC, USA
Posts: 3,089
Re: Electrician question - Voltage coming through an off switched outlet.

Broken neutral somewhere. Might be a loose neural connection.

B D R
gunny is offline  
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the BMW Luxury Touring Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in











Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page
Display Modes
Linear Mode Linear Mode



Similar Threads
Thread Thread Starter Forum Replies Last Post
Zumo 550 voltage question Dann323 RT Series 2 Mar 30th, 2012 6:08 pm
more power (voltage outlet) baker K1200LT 4 May 9th, 2009 8:28 pm
Accessory outlet question??? motorman587 K1200LT 3 Feb 3rd, 2007 6:10 pm
Power Outlet Question dwillie K1200LT 7 Aug 30th, 2006 6:11 pm

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome